AEW21.1 and MiniPLC

Tagged: ,

This topic contains 0 replies, has 1 voice, and was last updated by  Jan Vidim 8.7. 2008 07:16.

Viewing 1 post (of 1 total)
  • Author
    Posts
  • #12499

    Jan Vidim
    Keymaster

    When integrating the M-Bus AEW21.1 converters to MiniPLC beware of the timeout settings in the comm parameters of each datapoint (Special params – Telegram timeout): if there are communication problems, increase this value from default 400 up to 2000 ms.

Viewing 1 post (of 1 total)

You must be logged in to reply to this topic.